What is the minimum size aluminum equipment grounding conductor for an individual branch circuit supplying a twist-lock receptacle rated at 20 amperes?

Prepare for the Code Standards and Practices Level 1 Test. Test yourself with multiple choice questions, flashcards, and explanations. Ensure success with our comprehensive study materials!

Multiple Choice

What is the minimum size aluminum equipment grounding conductor for an individual branch circuit supplying a twist-lock receptacle rated at 20 amperes?

Explanation:
Sizing an equipment grounding conductor follows the overcurrent protection rating. For aluminum conductors, NEC 250.122 specifies the EGC size based on the circuit’s OCPD. With a 20-amp branch circuit, the aluminum EGC must be 8 AWG. This larger size compared with copper reflects aluminum’s characteristics and ensures a reliable fault path to trip the breaker. The twist-lock receptacle type doesn’t change this requirement; the protection is still determined by the 20 A rating. So the minimum aluminum EGC size is 8 AWG.

Sizing an equipment grounding conductor follows the overcurrent protection rating. For aluminum conductors, NEC 250.122 specifies the EGC size based on the circuit’s OCPD. With a 20-amp branch circuit, the aluminum EGC must be 8 AWG. This larger size compared with copper reflects aluminum’s characteristics and ensures a reliable fault path to trip the breaker. The twist-lock receptacle type doesn’t change this requirement; the protection is still determined by the 20 A rating. So the minimum aluminum EGC size is 8 AWG.