Per 600.7(A)(2), what is the minimum size equipment bonding jumper required to be connected from a grounding terminal on a switch for a neon tubing outline lighting circuit protected at 30 amperes?

Prepare for the Code Standards and Practices Level 1 Test. Test yourself with multiple choice questions, flashcards, and explanations. Ensure success with our comprehensive study materials!

Multiple Choice

Per 600.7(A)(2), what is the minimum size equipment bonding jumper required to be connected from a grounding terminal on a switch for a neon tubing outline lighting circuit protected at 30 amperes?

Explanation:
Bonding jumpers must be sized to provide a reliable fault path, based on the circuit’s overcurrent device rating. For equipment bonding in neon-tube outline lighting, the size is dictated by NEC 250.122. When the circuit is protected at 30 A, the minimum copper equipment grounding conductor size is 10 AWG. A smaller conductor (12 or 14 AWG) would not meet the requirement for a 30 A circuit, while a larger one (8 AWG) would be acceptable but isn’t the minimum. So, the smallest size that satisfies the rule is 10 AWG copper.

Bonding jumpers must be sized to provide a reliable fault path, based on the circuit’s overcurrent device rating. For equipment bonding in neon-tube outline lighting, the size is dictated by NEC 250.122. When the circuit is protected at 30 A, the minimum copper equipment grounding conductor size is 10 AWG. A smaller conductor (12 or 14 AWG) would not meet the requirement for a 30 A circuit, while a larger one (8 AWG) would be acceptable but isn’t the minimum. So, the smallest size that satisfies the rule is 10 AWG copper.

Subscribe

Get the latest from Passetra

You can unsubscribe at any time. Read our privacy policy