How many volume allowances must be taken for each device installed in an outlet box?

Prepare for the Code Standards and Practices Level 1 Test. Test yourself with multiple choice questions, flashcards, and explanations. Ensure success with our comprehensive study materials!

Multiple Choice

How many volume allowances must be taken for each device installed in an outlet box?

Explanation:
In box-fill calculations, every device mounted in the box uses up space equivalent to two conductors. The device’s yoke or strap counts as two conductor-volume units toward the total, regardless of the wire gauge. So for each device installed, you must add two volume allowances to the box-fill calculation. A duplex receptacle is one device, but it still accounts for two volumes. The actual cubic inches required for those conductors depend on wire size (for example, #14 uses 2.0 cubic inches per conductor), but the device itself consistently adds two volume units.

In box-fill calculations, every device mounted in the box uses up space equivalent to two conductors. The device’s yoke or strap counts as two conductor-volume units toward the total, regardless of the wire gauge. So for each device installed, you must add two volume allowances to the box-fill calculation. A duplex receptacle is one device, but it still accounts for two volumes. The actual cubic inches required for those conductors depend on wire size (for example, #14 uses 2.0 cubic inches per conductor), but the device itself consistently adds two volume units.